Tester101
  • 131,561
  • 78
  • 320
  • 610
Dusty580
  • 21
  • 1
  • 2
  • 3

1 Answers1

4

The average fixture has no need for 3/4" inch, particularly with homerun piping from a manifold. 3/4" is really only needed for tub fillers with larger tubs, or showers with multiple shower heads.

Running 3/4" hot water lines to fixtures will significantly increase hot water wait times, and should be avoided when not necessary (and for lavatory sinks, I'd strongly recommend 3/8" hot water supply lines).

Zhentar
  • 1,212
  • 6
  • 7
  • Any particular reason why I should use 3/8" for the bathroom sink and not other fixtures? If I was to use 3/8" for the sink, is there some kind of adapter to convert the manifold 1/2" outlet to 3/8"? – Dusty580 Feb 15 '15 at 03:28
  • Bathroom sinks have the lowest flow rates, and the least need for flow, and people are more likely to want hot water quickly. You can use a reducing coupling to switch from 1/2" tubing to 3/8" tubing – Zhentar Feb 15 '15 at 05:05